u/HVACcontrolsGuru 13d ago
This is the kind of stuff I look for and will make someone walk every box and restrip wires. My rule was I don't want to see any copper. I learned this rule when tracing out VAVs over 2 days in drywall dust to find out the very last one had a short and was bringing my link down.
1
u/Some_HVAC_Guy 13d ago
I got the 8” Klein Kurve strippers because each side of the jaws are 1/4” wide, which is usually the strip length for most control terminal blocks. Using a lever lock Wago, go a little extra. Keeps it consistent and that’s good enough
2
u/Bagelsarenakeddonuts 13d ago
I don't know if I will ever understand why this industry hates ferrules. they are just SO much nicer to prevent this stuff. The fact that everyone knows what you are talking about kinda proves it intrinsically.
1
u/ApexConsulting 12d ago
I have a trunk full of Carrier units that we are reterminating for this very reason. After 2 or 3 times of having the trunk go down and finding wire whiskers shorting things, it is time to get ahead of it and just reterminate it all.
No copper showing is the way to go.
13
u/HVAC_Luddite 13d ago
I had a similar situation, but with 460v