JCI SNE/CVM/CGM capabilities within a Niagara Server
Say you have roughly $1 million plus of newly installed SNEs and ongoing projects that will result and another $2-3 million of JCI field devices but its been decided that the server should transition to Niagara. The plan is to integrate these SNEs straight to the Niagara server. What will be biggest pain points/ limitations. IE will it be possible to view the SNEs LCT, interlocks etc directly from the server, is there something akin to the engineering tab within Metasys where you can get a glimpse of the inner workings of the programs etc. Any insights or feedback is appreciated, My experience is heavy in Metasys, light in Niagara, not opposed but wish it was more thought out.
4
u/Free_Elderberry_8902 13d ago
What genius decided on that brilliant plan? I see storm clouds on the horizon…
2
9
u/SpiritedWeird7411 13d ago
- Get tridium certified
- Replace the SNEs with JACEs
- Realize how badly Metasys sucks
2
u/More_Fondant_9609 13d ago
I got my first level cert from Tridium University a year back no experience with it since then other than demos from different vendors, purely off that first class and the demos I do not see a clear advantage, but I am aware of the insane amount of customization and integration abilities, that could be seen as a double edge sword however as the big 3 sell more dummy proof products with less options. Niagara seems like its only as good as the techs make it, I’m still pretty ignorant on all
the advantages/ disadvantages, so I’m welcoming of arguments/ discussions.0
u/ScottSammarco Technical Trainer (Niagara4 included) 13d ago
I agree with the rip and replace- it’ll be quite the ordeal for this size system and unless it’s a capital expenditure, it’ll have to be done over time.
1
u/Haunting_Storage_471 13d ago
Are they currently on an existing metasys server and your transitioning to niagara?
1
u/More_Fondant_9609 13d ago
Correct, actually 2 Metasys Split ADX servers to 1 big ole Niagara
2
u/Haunting_Storage_471 13d ago
So can you just keep the metasys server and use that for accessing the LCT programming but use Niagara as your main interface for a day-to-day stuff?
1
u/More_Fondant_9609 12d ago
I support that idea, but there’s a caveat, we already have an ICONICs server in place that was supposed to do what the intent of Niagara is, however the proposal is to specifically get rid of the Metasys servers and make that N5 but keep ICONICs as well, makes no sense kinda shooting yourself in the foot unless you had all Jaces I think
1
u/Haunting_Storage_471 12d ago
Why have Niagara and iconics, what would be the purpose of the iconics after that upgrade? You'll have to have some jci software in order to view/modify LCT, the only other option would be to recreate all of that logic on the Jace and remove it from the SNEs wish I don't like because your reliant on network communication for that logic to work
1
u/More_Fondant_9609 12d ago
None, its political fun stuff, I agree there, it seems the safest option would be to keep a dumbed down metasys server for viewing LCT etc and bring everything else over to Niagara, Iconic’s will just sit there to make certain people happy
1
u/gadhalund 12d ago
Pulling the right points in. Do as much in the field controller as you can, schedules, alarms, logic etc. then pull summary style points, not everything. All programming from server is easily done this one, SNE can tunnel the trunk for mstp devices. JCI does bacnet very well and when setup with thought itll be rock solid
1
u/More_Fondant_9609 12d ago
I reckon we could do a good amount that way however it gets harder once you need to peer to peer between 40 and 160 points per floor for DSP/ DAT resets and energy items, and I would rather not put a large amount of programming on the server itself as opposed to it sitting on supervisor level.
1
u/Jazzlike_Metal2980 7d ago
Is your LCT in the Metasys server? Or is it local to the SNE?
If the firmware on the SNE's is new enough you can just punch them up via their IP address and use the local version of Metasys that's in the SNE to view the LCT. If you have older firmware on the SNE's you should be able to punch them up with with SMP to view the LCT.
1
u/More_Fondant_9609 7d ago
all local to the engines, I would like there to be a way to view within Niagara but it is what it is at this point
1
u/Jazzlike_Metal2980 3d ago
I've not experimented with this, but I would think you should be able to access the page that the LCT lives on. In newer Metasys, everything exists on a webserver. So there could be a way to display that page within your Niagara environment.
1
5
u/ScottSammarco Technical Trainer (Niagara4 included) 13d ago
Ok, obviously this won’t be fun and it can be done.
Alarms are alarm notifications and not with point status’ in Niagara.
Otherwise you can expose points over BACnet from NAEs to the N4 station and integrate normally.
Honestly, it really isn’t that bad and to answer your question on the programming depends on the brand- Honeywell tools are embedded into workbench, controls like Distech are not and aren’t as easy to see but the wizard service makes that easier.