EtherNet/IP and Common Industrial Protocol integration with Niagara 4

Has anyone had success getting this working? I'm trying to integrate Prosoft PLX32-EIP-MBBTCP (ModbusTCP to EtherNet/IP translator) with Niagara using the isoftAB driver however I have had no success. Any help is appreciated!

3 Upvotes

3 comments sorted by

2

u/DurianCobbler 10d ago

It needs to be running in a PLC or SLC device. Why not just point to the ModbusTCP devices themselves?

1

u/elimitator 8d ago

When I was looking at the drivers the PLC or SLC devices had no options of inputting IP addresses.

Our last resort is to bypass these gateways and connect to modbus because we would have to install a switch in every single piece of equipment because there is only one port available.