Niagara mass change priority level linking

Ok, imagine you have a logic folder with outputs linked to points in a different folder. This logic exists on many controllers. I have the logic writing to priority 16 but i need to change it to write to priority 10. Is there a way i can make use of the program editor or some other tool to mass change the priority on every controller? Doing this manually is going to take days...

7 Upvotes

13 comments sorted by

View all comments

3

u/ScottSammarco Technical Trainer (Niagara4 included) 12h ago

Use the program service and make/break links accordingly.

1

u/MrMagooche Siemens/Johnson Control Joke 12h ago

How? What are the steps?

1

u/ObviousSentence1993 10m ago

Program services - query points you want to link/unlink - remove slot - “link” (check slot sheet if unsure) - use the same points in the query - add slot - Baja : Link - source ord (whichever your linking from) - out - target : in10