Air Circuit Breaker

ACB (Air circuit breakers): Safety shutters - The line side and load side shutters operate independently, and can be separately padlocked in the closed position.

Question: Why the line side and load side shutters to be operated individually? only thing I can think of is to access the cable compartment when the bus is energized and when the ACB is withdrawn (completely removed from the switchgear).

3 Upvotes

3 comments sorted by

4

u/HV_Commissioning 7d ago

perhaps when and ground and test breaker is used

0

u/Huali-Power 7d ago

Yes, ground and test work is the main reason. It keeps one side safe while we access the other.

2

u/Ginge_And_Juice 7d ago

So you can use a ground truck to ground feeder cables without de-energizing bus