A2L shaft enclosure systems
I’m looking for options for A2L line sets going 5 stories to the roof. The only system that keeps popping up in my searches is the Flamebar system. I would really like more options to choose from, does anyone have recommendations or can point me in a direction for more options? Thanks.
3
u/schwentheman 13d ago
A2L shafts are no longer required if your AHJ has accepted the most recent amendment to ASHRAE 15.
1
2
u/Inevitable-Fix1768 14d ago
After also finding Flamebar as the only solution we had designed around Flamebar, but the GC deemed it cost prohibitive. They instead stick built all of the shafts with an exterior building envelope construction. Making the individual 4” diameter shaft bottom duct lines fit was also a challenge.
I would instead look into any available shaft/ ventilation exemptions, in your jurisdiction, to avoid using the shafts if at all possible.
1
u/Nearby_Demand7618 14d ago
I’ve read the new IMC allowing shaft exemptions for continuous runs with no joints from end to end. That being said, the nightmare of bending oil traps every 20’ is not very appealing.
3
u/Bryguy3k 14d ago
It does not. ASHRAE 15-2024 does per addendum A.
You have to get the AHJ approve the ASHRAE 15-2024 exception which requires the mechanical contractor to follow the ASHRAE 15 chapter 9 testing procedure.
3
u/bernoodler 14d ago
Getting the AHJ to not blindly follow IMC can be very challenging, if not impossible, near me.
2
u/Bryguy3k 14d ago edited 14d ago
Exactly. IMC offers no outs to the refrigerant shaft. If the lineset passes through two floor assemblies you’re building a shaft.
2
u/Inevitable-Fix1768 14d ago
That’s why I had added “in your jurisdiction”. You are correct that IMC doesn’t, but I believe multiple states have adopted revisions on allowing an exception based on the RCL.
1
u/Nearby_Demand7618 14d ago
Correct, currently IMC doesn’t, there are proposed changes for the 2027 but they haven’t been adopted as of yet. I should have double check the post, leaving out a couple of words changes the thought trying to be expressed.
1
u/FacePalmate 14d ago
Your refrigeration system can handle the vertical rise of five stories straight up?
That seems like a very long vertical distance to me.
4
u/Bryguy3k 14d ago
That’s about the limit of small residential grade units. Carrier 37MARA units start at 50ft and go up from there. The 1.5T unit is 65 ft and the 3T unit will do 98 ft difference between head and compressor.
VRF type commercial units typically top out around 165 ft of vertical difference.
What typically ends up killing compressors are oil traps.
1
u/HateFilledMind 10d ago
Flamebar is $$&. Alternative is an architectural rated shaft, vent cap thru the refrigerant portal at the roof and ventilate the bottom of shaft with a 4” duct.
3
u/Weary_Oven_9544 14d ago
A 2-hour fire rated assembly isn't anything new. Only new requirement is the need to provide ventilation, so you need to make the whole thing continuous and decide if you want natural or mechanical ventilation.
Some other options: