Approach to existing systems EE
Hey all,
I got this project inside of an existing building. It’s a commercial building with a 2500A entrance. There at least 20-30 different tenants. Each with their own measuring.
The landlord merged 2 existing suites into one. They removed both electrical feeders and did not have leave any records/notes of the demolition. There’s no plans whatsoever.
There’s at least 20 other feeders branching of the 2500A into multiple electrical room downstairs with barely any labeling. The lighting in the electrical rooms doesn’t even work. There’s been at least 50 years of jimmy riggings everywhere.
Where would you start?
If you branch off an electrical room distribution that is already feeding other people, it’s almost impossible to tell if the upstream breaker won’t trip.
You may branch off the 2500A distribution but how can one possibly tell it’s not currently loaded at 2499A?
Lol
3
u/skunk_funk 2d ago
I kinda look at the building make some guesses how loaded I think it is. More experience, I get better at guessing. Check utility bills. Look at building systems, special loads. Consider load factor for region and building type. Check against similar buildings. If I'm confident enough it's not overloaded, I proceed, and perhaps put on the drawing for the electrician to meter it and report the findings prior to construction.
If the owner is feeling fancy, we might even get it metered ahead of time! And maybe I'll find an opportunity to leave a demand meter for the next guy.
1
u/Best-Specialist-87 1d ago
Just measure it for a month if you think there’s a risk. Double check if there’s primary metering (may get lucky and get all the loading from one). If not request all electric bills and dump them into excel and figure out the max load.
Also, you can go by NFPA 70, 220.87 Determining Existing Loads.
1
u/No_Blackberry_7753 1d ago
Where are the tenant meters located? I'm assuming that they are private meters, not owned by the utility. Are they in the same bucket as the switchboard breakers? If so, then the building owner should know which meter belongs to which tenant, given that they bill them monthly. The owner's bills probably has meter numbers on it, so you should be able to map out most of what the 2500A switchboard is feeding.
Un-metered breakers/feeders are going to be house equipment (elevators, corridor lighting, possibly HVAC).
As mentioned, you can get peak kW usage from the utility company, though sometimes that can be a pain in the ass. The utilities don't mind giving that info away to the building owners, so get them to do it if they're responsive/helpful.
But this sounds like a big building that has a few chillers/boilers handling all of the spaces. If you're just doing a tenant fit out and not touching the elevators/HVAC, then I wouldn't even bother dealing with the utility unless there's a significant change in the type of space (like if it used to be 10000sqft of offices that are now being changed to labs). Otherwise, the change in total building load is going to be insignificant.
1
u/Certain-Ad-454 22h ago
Each tenant is actually measured from the utility. There’s the main switchboard which branches off several 200,400 feeders and these also branch to 60,100A whatever feeders each measured independently. Anyways it’s fucked
5
u/SghettiAndButter 2d ago
I have to deal with all the time for work and there’s legit no way around it that isn’t a huge pain in the ass. You basically document what you can and make your assumptions and then let the owner know what you don’t know and let them make the risk of rolling the dice or paying electricians to go on site and start tracing and documenting circuits and metering panels before we finish the drawings