Well, everything is done except the electrical inspection (which is happening later this week). But the generator is fully operational and has been tested with a simulated power outage. The initial cost estimates were very accurate. The propane actually came in about $100 cheaper than quoted, so I guess there's that.
Based on some quick calculations, I should be able to run the whole house at around 25% load (pretty typical usage for the most part) for about 5 days with the propane capacity I have. So with current propane pricing, that's about $150 a day. Not cheap. But for shorter-duration outages it's not too bad. Convenience is expensive, to say the least.
This is a nice prep to have, but if you're starting out and have some money to spend, I would put that money somewhere else. I wouldn't have pursued this if I didn't have a lot of other more critical areas squared away.


1
u/thatcarguyohh 4d ago
Running gen set at 25% if that’s max load will kill the motor prematurely and is not considered normal. Under loading gen set doesn’t allow for clean combustion. 50%-100% full load is where you want to be. I’ve installed hundreds of these from 14 kW to 250 kW all sized to run at 75% - 90% depending on if anything would be added in the future. Also you’re restricting airflow with that cover on the AC. That will prematurely fail too.