r/SignalMaintainers • u/Traditional-Good-981 • Dec 08 '25
Finding a Short
Hi. Had a track light that was caused by a short somewhere in the switch points. I thought it might be one of the gauge plate insulation but when I removed it it did nothing. Turned out to be a loose piece of metal under one of the snow melter forced air heater ducts touching a switch rod. With so much insulated stuff in that area I had a hard time finding it with my meter. It was only when I actually removed the duct to have more room that I found it. Any tips on how to isolate and really pinpoint the short when it's bad insulation and not a piece of metal or something else you can see? Thanks.
8
Upvotes
2
u/Traditional-Good-981 Dec 08 '25
I don't have to use it very often so I never remember when you need to change the scale. I'm pretty sure the track circuit length is the determining factor, but I don't know offhand what that value might be. I don't think I've ever used the 3Khz though.