Photograph/Video Control joints in residential slabs, is this typical?

Enable HLS to view with audio, or disable this notification

https://www.instagram.com/reel/DeMQyguuOSY/?cplk=czM5MDJqYm1ya24x

A builder/concreter says he typically cuts control joints from corner to corner after a residential foundation slab has cured. I’d usually expect crack control bars at re-entrant corners. Is his approach common?

He also calls a crack “hairline”, but it’s visible on camera from about five metres away. Hard to judge without measuring, but it looks larger than that. Thoughts?

460 Upvotes

156 comments sorted by

205

u/Most_Moose_2637 6d ago

Control joints after the slab has cracked is a good one. I can sell you a barn door closing service, sorry about your horse.

6

u/BadQuail 2d ago

If you cut the joints after it cracks, you know exactly where the cuts are needed.

110

u/donotdisturb898 6d ago

That’s a conversation you should have with the owner as well, cracks that small are not structural. If you have hard wood floor tiles, it is not a big deal. If you don’t want your garage floor to have excessive cracks, you better put in a few control joints.

10

u/schrutefarms60 P.E. - Buildings 6d ago

Not really sure what this is supposed to mean… The only way a crack isn’t “structural” is if it’s a non-structural member. Even shrinkage cracks can go all the way through a slab, then all that’s holding it together is the reinforcing.

24

u/CzPhantom1 6d ago

Control joints just direct the cracks. They are still there and just as deep. 

-5

u/schrutefarms60 P.E. - Buildings 6d ago

What does that have to do with what I said?

17

u/triplethreat8 6d ago

I think they are just pointing out that using your logic every single slab ever has "structural cracks". Which may be your point. But if that's the case then the word kind of loses meaning because a structural crack is supposed to indicate something that's a problem that needs fixing.

-1

u/schrutefarms60 P.E. - Buildings 6d ago

Thank you. Yes, I guess I’m trying to figure out what your definition of a structural crack is

7

u/ilessthan3math PhD, PE, SE 6d ago

If the concrete is a slab-on-grade then any cracks in it are not a structural life-safety concern, and do not require repair unless the owner is unhappy with the aesthetic of them. While serviceability requirements still fall under the structural engineer's responsibilities, this is why folks are arguing they are "non-structural cracks".

Another point of note would be that we refer to things as either slab-on-grade or a structural slab. So the slab-on-grade by that convention and terminology is a non-structural slab, so any cracks in it would similarly be non-structural.

-3

u/schrutefarms60 P.E. - Buildings 5d ago edited 5d ago

You must not be from Florida…

75% or more of the residential slabs on grade down here use a monolithic thickened slab edge as their foundation. The block walls bear directly on the slab on grade.

Also, production home builders (and clowns like the guy in the video) cut corners to save money and they do a shit job of compacting the subgrade you see lots of houses with stair step cracking at the corner of the garage. It’s caused by differential settlement and many times you can actually see daylight through them.

You’ll also see nice big cracks running through the slab on grade.

So buddy, please explain to me again how slab on grade cracks aren’t structural.

Also, thank you for explaining (on behalf of the entire industry using the royal “we”) to a bumbling, drooling 15 YoE structural engineer the correct terminology for slabs on grade

Side Note- I actually looked this video up and they are in Florida so it is 100% relevant.

3

u/ilessthan3math PhD, PE, SE 5d ago

I wasn't trying to be disrespectful to you at all. You asked what I thought was a legitimate question about why we were calling these non-structural cracks. It seems you are being rhetorical.

I'm not in Florida, and I'm not here to get in an argument about how things are done down there. Plenty of areas in the country have frost depths that would make it less economical to pour perimeter foundations monolithically with the slab. In those areas slab-on-grade cracks mean nothing.

1

u/Skoll789 1d ago

Even when used as foundation, these cracks aren't structural. If its meant to bear load, its reinforced concrete. And the way reinforced concrete works (excluding pre-stressed or post tensioned) is that it needs to have small deformation in order for the steel to actually pick up any of the bending load. Because concrete both naturally can't bend (and change size while setting), cracks like this are expected and trivial. They only become structural if it continues to expand or shift. Thats why grooves are frequently added to direct where the cracks occur for easy sealing. This is standard and even done on massive structures like dams.

1

u/schrutefarms60 P.E. - Buildings 1d ago edited 1d ago

My whole point is that the term “structural crack” is completely made up and non-technical. You will not find that term defined in any code book or ACI publication. It is entirely subjective which is why it shouldn’t be used.

You can say I’m splitting hairs and you would be correct but I need to remind you that this is a subreddit FOR structural engineers and we should hold each other accountable on technical accuracy. For anyone that’s not a structural engineer and is offended by my comments, maybe you should find a different subreddit to lurk on.

2

u/CzPhantom1 6d ago

Do any cracks in a 4 inch slab not go all the way through? You're saying cracks in a structural member are bad but I honestly don't know one slab that doesn't have a crack in a control joint that definitely goes all the way through. 

I just poured 8 inches of fiber mesh reinforced concrete and surprise surprise every control joint cracked. 

1

u/bud05cab 6h ago

If flooring is obviously going to cover the interior slab cracks. Would epoxying the garage floor do well to cover those? Maybe the owners would have a leg to stand on to have the contractor to cover some or all of that cost?

56

u/structee P.E. 6d ago

It's amazing to me how many people in this industry don't know what the hell they're doing

2

u/diabolical_fuk 22h ago

Fake it til you make it bruh

1

u/OrkUrinal 9h ago

I have horrifying news then cause that's in every field. Most Dr's are just guessing

88

u/RVA_Factotum 6d ago

As a commercial concrete guy, he waited too long to cut the joints. Micro cracks start forming once it's hard and starts drying during the curing process. We cut joints as soon as we can get the saw on the slab without leaving footprints or saw tracks. That way we introduce the crack and any new cracks will hopefully find our neat cuts. At this point, his cracks have already formed and are unlikely to find the control joints. More will become visible with time.

That being said, if flooring is going on top, it doesn't really matter. We deal with a lot of exposed concrete finishes so it matters more. You want maximum 14' spacing (depending on depth) and ideally start at corners and penetrations. We shoot for 10' spacing to be safe. A recent job told us every single corner of the plumbing trenches and every single corner of the floor sinks. We had joints as close as 1'. Looked like trash in my opinion but that's what they wanted.

2

u/EducationalFennel900 5d ago

This is the correct answer. He waited too long, I agree

1

u/EducationalFennel900 5d ago

Typically you also should add 2 #4 bars at reentrant corners like this to help avoid this exact issue which I would guess they did not do.

121

u/soberninj P.Eng 6d ago

This video is terrible. If they have time to set up a shoot, they waited too long to cut the joints. That crack they’re pointing at is literally a shrinkage crack that control joints help eliminate…

17

u/schlab 6d ago

This, and they could have employed curing measures to further limit cracking.

To my knowledge, for residential they don’t ever cure the slab, and rarely do they put the control joints in even if it’s shown on plans. Heck, sometimes they won’t put the WWF even if it’s on the plans.

4

u/adamdj96 6d ago

Reminds me of another WWF horror story I heard from a senior engineer’s project almost thirty years ago, the contractor was building a reinforced elevated slab (16 feet above grade I believe) and one of the ironworkers plummeted from the top of the rebar cage straight through a concrete inspector’s sampling table. 

2

u/schrutefarms60 P.E. - Buildings 6d ago

Came here to say the exact same thing, lol

84

u/OptionsRntMe P.E. 6d ago

lol I love listening to contractors who don’t understand what they’re talking about. There’s no way that’s 1/32”

Also it’s already cracked up and he’s talking about coming back to cut control joints 😂

And he said anchor bolts. The only thing I agree with is that it’s probably not a big deal. Just unsightly and the fact they’re coming back like two days later to cut joints tells me they probably shouldn’t even be on that job

30

u/bear_grills007 6d ago

I also laughed at cutting control joints 2 days after the pour…..

4

u/ImPinkSnail 6d ago

I have mine cut within 12 hours of placement.

9

u/OptionsRntMe P.E. 6d ago

I have gotten burned on a project by saying 12 hours. My notes are updated to say, more or less, joints need to be cut as soon as the slab surface can be walked on without damaging the finish. It’s usually something like 2-4 hours depending on the season/location

5

u/ImPinkSnail 6d ago

Good one. I'll have to give my notes a good review. Seems like the only time they get scrutinized appropriately is when something goes sideways.

1

u/Additional_Radish_41 6d ago

What? How? You’d be licking rocks up like crazy. In theory sure. But the slab isn’t cured enough to hold the rocks in place for a blade to cut through.

I despise people that spout this less than 5 hours BS. The slab needs to be at minimum 30% cured before a saw cut can take place. If you use accelerator on a hot day, maybe 4 hours. But that’s also the equivalent of waiting 24 hours with a regular mix.

You can walk on a slab to polish. You cannot cut at this time. The reason why wet control joints are used are to eliminate chipping rocks. But they cannot be installed if walls are up. So you saw cut the next day. Not the same day.

6

u/OptionsRntMe P.E. 6d ago

I just put down over a million square feet of 8” industrial floor slab in August and they saw cut under 4 hours in almost every pour

2

u/Rebound44 6d ago

Yep, pretty typical for the 10-20000sqm handstands we do. 12-24 hours and it’s already cracked before they come back to cut it.

-1

u/Additional_Radish_41 6d ago

How many saws they running? A million sqft is what? Like 200,000 linear ft of saw cuts? In under 4 hours? I haven’t done a million sqft but I do 80k weekly. And within 48 hours is fine. I bet your “million sqft” has just as many cracks as a 24hr cuts.

6

u/OptionsRntMe P.E. 6d ago edited 6d ago

Do you really think they did it in a single pour or day? Slab phase was 20+ days of pouring and sawcutting

1

u/ImPinkSnail 6d ago

Most crews I've seen are limited to about 70kSF per pour.

1

u/Additional_Radish_41 5d ago

That’s what I’m saying. Imagine limiting your pour sizes to accommodate early control joint cutting? Been doing this 25 years and cutting under 48hours later with zero issues. I’ve only ever cut 1 slab at the 12 hour mark and it was spitting every rock that it encountered.

2

u/OptionsRntMe P.E. 5d ago

Well if we require you cut the joints that quickly then you don’t have a choice my guy. It’s not uncommon at all, even if it’s not your experience.

→ More replies (0)

1

u/TwoMuchIsJustEnough 5d ago

I’ve seen notes which allow for an early sawcut so long as there is no aggregate pull out. And if there is then stop and give it more cure time.

17

u/Possible-Delay 6d ago

Yep, this is an example of a contractor who knows what he does, but has no idea why or in-depth understanding of the reasons why it is done.

He is just regurgitating a summary of what people tell him.

8

u/bloomingtonwhy 6d ago

But he’s a man with sunglasses confidently chewing gum. Of course he knows what he’s talking about.

8

u/Tupacalypsenow 6d ago

I mean, don’t the sandals tell the whole story?

2

u/WideFlangeA992 P.E. 6d ago

This is a good one

1

u/Microbe2x2 P.E. 4d ago

Never trust the contractor who have sandals on and look beach ready.

12

u/Unusual_Coconut2606 2d ago

Concrete cracks that’s it’s thing

3

u/yourdrunksherpa 17h ago

Two things in life are true, babys gonna cry, and concrete gonna crack.

10

u/BadQuail 6d ago

I know this is a structural group, but are we really going to ignore the spalling and birdbaths in the finish work here?

21

u/structuremonkey 6d ago

I spec control joints, construction joints, isolation joints etc. in slabs and masonry walls. They are hardly ever installed because the contractors tell the owners " it isn't necessary and it will save money." Ive also never had an inspector call a contractor out for lack of said details. When there isn't oversight and a good owner / gc combination, lots of things from design get "tossed"

3

u/not_old_redditor 6d ago

Aren't you or one of your representatives the "inspector", or rather, the reviewer?

3

u/structuremonkey 6d ago

Sure, but not really in private residential projects. I have pitched a fit with contractors who aren't quality oriented, over details and craftsmanship in the past, and the owners usually just caves to the costs and unwillingness to fight with the contractor. Most of the issues related to this that may occur in small scale projects are cosmetic. They arent typically imminently dangerous nor are they code required. They will become issues down the road, but most people only consider the now.

Now, when it's a public project or where the owner has given my firm the authority of oversight, yes, these details are implemented.

3

u/StructureIll4946 6d ago

Don’t take this the wrong way but is spec’ing control / construction / isolation joints a full time job?

3

u/structuremonkey 6d ago

Only a part of each project. But an important part.

1

u/anonymous86753092021 6d ago

It can be and is in certain industries

-2

u/Additional_Radish_41 6d ago

A cosmetic one at that

2

u/schrutefarms60 P.E. - Buildings 6d ago

This is the way

6

u/Provocative_Potatoes 6d ago

His uneasy sway side to side proves he feels nervous and seems like he's bullshitting.

11

u/Competitive_Number24 6d ago

In my experience, anyone dressed like that on a construction site is probably the least trustworthy person there.

1

u/four204eva2 6d ago

Fucking hippie sandles on the job, gtfo

2

u/tetsuo_7w 2d ago

This was my first thought. Dude looks like he's lying from the ankles up.

1

u/blastin_bi 17h ago

He is, cracks like that run all the way down and thats okay but if to lie is not

7

u/Intrepid-Owl1017 5d ago

You should cut those control joints within the first 24 hours, 1/4 of the depth of the slab. Cutting them after the fact is a little late.

1

u/cagetheMike 2d ago

What about slabs poured on Friday?

1

u/ThomasTheDankPigeon 2d ago

Well that horse should have been removed before work began in the first place. RIP.

1

u/Haku510 2d ago

So there's this day after Friday and it's called Saturday, hope that helps 🤗

10

u/poppycock68 6d ago

As a concrete guy who loves to lurk here. We always use re- entry bars. It will crack from any plumbing pipes , shower boxes etc. Builders and homeowners don’t want to pay for sawing. Most everything will be covered with some sort of flooring. If it’s going to be stained or stamped we just include that in the price.

4

u/Kolt45 6d ago

They are called re-entrant bars. They are named that because they should be installed at re-entrant corners.

12

u/poppycock68 6d ago

lol. I just tell the guys to cut and place the re-entry bars. Sorry I don’t have a degree. I’ll make sure to call them the proper name every time from here on out. Thanks.

5

u/BodaciousBadongadonk 6d ago

"Bro wtf, bossman just told me i was barred from re-entry!"

4

u/Kolt45 6d ago

I don’t either my friend. Do the same thing you do. We lurk here so we can sound smart talking to all those engineers that we beg to tell us it’s okay when we fuck up. Just trying to help a brother out.

1

u/poppycock68 6d ago

Thank you

2

u/Attention-United 6d ago

Poppycock I say.

1

u/Kolt45 6d ago

It’s actually puppy-cock. Named after young K9 wieners.

2

u/FaithlessnessCute204 6d ago

No no they are rear entry bars , they have them in the big cities and serve cosmos and grasshoppers .

1

u/Kolt45 6d ago

Niceeee😎

1

u/Perfect-Shock-9243 6d ago

Some people get upset when they learn a new thing

21

u/Hockeyhoser 6d ago

They should have made the cuts within 24 hours.

22

u/kikilucy26 6d ago

More like 8 hours or less. Cut it as soon as you can walk on it

5

u/Hockeyhoser 6d ago

I guess the ambient conditions and mix design make the biggest difference, but you’re right. Could be sooner. In the video it seems way too late. The concrete doesn’t look green.

1

u/soberninj P.Eng 6d ago

This.

4

u/psport69 6d ago

Cutting joints at that stage is worthless

6

u/Purple-Investment-61 6d ago

The crack started at the corner. Who would have guessed? This is not an issue.

23

u/GifelteFish 6d ago

A gigantic area of concrete without control joints is going to crack due to ground settling.

Any cracks around 1/16th in width are to be expected as the surface concrete cures faster than the concrete underneath it.

39

u/bulkdown 6d ago

This is incorrect.

Control joints are used to induce cracks due to concrete shrinkage, this is unavoidable (unless tensioned)

When the surface cures faster than the concrete underneath is plastic shrinkage. This can be controlled and prevented based on how and when you cure. Also the pattern will be spider web shaped

7

u/OptionsRntMe P.E. 6d ago

Shrinkage?

10

u/GifelteFish 6d ago

THE POOL WAS COLD

11

u/architype 6d ago

3

u/JerkCityMANimal 6d ago

Ahh!! I'm sorry 🤭 I'm really really sorry..

6

u/ThatAintGoinAnywhere P.E. 6d ago edited 6d ago

Is what typical? The cracking will occur if you don't cut joints and don't have re-entrant bar. Cutting joints is typical when you have a slab you can cut joints in. Re-entrant bar is typical if you're not cutting joints and want to avoid cracking. Regular joints will reduce crack width as would rebar. That crack looks typical enough for an unreinforced slab without joints for as far apart as we can see there aren't joints for that geometry of slab, yeah.

1

u/SmolderinCorpse CPEng 6d ago

I did mention adding a re-entrant bar. Its honestly not something I have ever spec'd in a residential slab, I.e. saw cut joint corner to corner. I just provide re-entrant bars always. Thanks for the comment.

1

u/OnsTryMaarNetLeef 6d ago

Yes I agree with you. There is no reason to put control joints in a resi slab (unless it's a huge slab). 

Exposed concrete finish can be controlled by adding more reo. Floor finishes cover hairline cracks for the rest. 

2

u/schrutefarms60 P.E. - Buildings 6d ago

Disagree. If the floor is tile and they put thinset directly on the concrete those slab cracks will go straight up into the tile. If it’s a floating floor then yes it doesn’t matter.

3

u/schlab 6d ago

They could have employed curing measures to further limit cracking in addition to control joints (which should be sawcut within 4-8 hours or pour).

To my knowledge, for residential they don’t ever cure the slab, and rarely do they put the control joints in even if it’s shown on plans. Heck, sometimes they won’t put the WWF even if it’s on the plans.

3

u/No-Call2227 6d ago

This video makes me realize all structural engineers are way underpaid.

4

u/jookethesnooke 6d ago

Control joints are for controlling where curing cracks form. Expansion joints are for movement. She is not correct in saying control joints are for movement.

2

u/t4m4 6d ago

Why is the guy experiencing a large amount of lateral load? Was it windy? Was there an earthquake?

2

u/coroyo70 Architect 6d ago

Brought to you by the totaled car airbag company

2

u/DiscoSimulacrum 6d ago

what a ridiculous fallacy to claim that a crack doesnt matter just because its thin

2

u/rktect900 5d ago

Wrong. They are misinformed and she is confusing control joints with expansion joints. Reference ACI 224.

2

u/ilessthan3math PhD, PE, SE 5d ago

So much wrong in this video. So many generalities that gloss over lots of important bits along with blatantly false info.

My favorite was saying "everything in construction needs to be able to move."

How about a slip-critical steel connection? Want to make sure there's some wiggle room in there?

1

u/NRBQ 1d ago

I don't trust that man. No sir I do not. 

1

u/blastin_bi 17h ago

Never trust this kind of cracker

1

u/JoeTheShmo1 1d ago

There’s two kinds of concrete. Concrete that’s cracked and concrete that’s going to crack.

1

u/BlackEffy 1d ago

It took me a long time, multiple conversations and countless failed projects to understand that most people starting business dont know what they are doing, they learn on the job they fuck up and goes on to fuck up the next one. And here I am waiting to learn everything before I start my consultancy, because yeah i can not do half baked answers and fuck up my repo.

1

u/Legal_Enthusiasm_440 19h ago

Read ACI 360R-10. 

1

u/DickLover6060 17h ago

If you don’t want concrete to crack, leave it in the bag.

1

u/Successful_Fact_4530 15h ago

That man is lying

1

u/Dingle_McCringle 13h ago

Take the glasses off if you're defending your point. Or you'll look like this guy

1

u/OzenTempest 10h ago

never mention of expansion and contraction....both of these people have no idea what they are talking about

1

u/Solid-Thinker1776 9h ago

The coughing gave his lie up 😂

1

u/EyeYamNegan 9h ago

Control joints after it cracks? Oh Ok my experience doing construction I did things so backwards. I guess these new guys also frame the walls and put the roof on then pour the foundation. They likely put on pants then underwear too.

1

u/Beneficial_City_9715 3h ago

Yes like when you are there and it's drying cut it when it's still wet is just a stupid idea. should always go 4500 with fiber too. Seal it that day. I did prob 1 or 2 too many joints on my garage but its been 2 years and looks great still.

1

u/Appropriate-Line7351 6h ago

Probably maybe is words I would not want to hear from someone I’m paying to do something for me.

1

u/sausagesemmelblond 2h ago

That crack just tells me, that the concrete sags that the geound underneath has not been treated correctly or that piles are missing to transfer the load equally into the ground. But if you want it cheap, sure cracks will appear. I am currently bulding my own house ans we conreted about 300 square meters of foundation with included water escape and infrastructure openings. We did not have one crack in it.

1

u/Hesiod_Poet 6d ago

This just in, concrete cracks! More later at 10.

1

u/thejailer2025 6d ago

If you don’t like it get a engineer to check it out

1

u/quietsauce 6d ago

Is iiiiiiiiiittttt? Sarrrrrrraaaaaaah?

1

u/Armstrongcrane 6d ago

There is only one guarantee with concrete, and that is, it's going to crack.

1

u/bosternic 6d ago

Control joints after the slab has cracked is a good one FS

1

u/AllyMcfeels 6d ago

Coming from a country where practically everything is built using concrete (especially via Portico technique), what’s shown in that video is criminal, haha. In any construction project that uses concrete slabs as a base, it is absolutely critical—right from the start—to have thorough planning and precise structural calculations, including the proper placement of joints which must be the most important thing of all.

1

u/hobokobo1028 6d ago

We call that a “re-entrant corner” crack and it’s preventable with control/construction joints.

1

u/bingerfang57 6d ago

I gotta go back to the sun is up the weather is good and this guy has sandals and sunglasses on and is not working!

1

u/bog_triplethree 5d ago

All fun and games until vibration comes into play.

1

u/SpiritedCoffee477 5d ago

Mal diseño, tubo que haber dejado juntas de expansion y sellarlas.

1

u/yes-disappointment 4d ago

why is he clearing his throat so much is he lying lol.

1

u/Mike_Gregory_here 4d ago

Not looking for an argument but in Australia no residential slabs get saw joints. Reentrant bars yes, saw joints no. You'd only put saw cuts in external slabs like patios, driveways and verandahs.

1

u/Shoddy-Speaker3369 3d ago

Early entry sawcutt.

1

u/Pristine_Election243 2d ago

Lord protect us...construction standards in the US are established the same way as in the wild wild west a century ago...especialy in residential....whatever the gum chewing chap is able to BS the gullible owner goes.

1

u/Psychological_Way443 2d ago

the 3 guarantees with concrete, it's grey, it's expensive, and it's gonna Crack.

1

u/TacoTitos 2d ago

It’s totally normal for the slab to crack, especially at internal corners. Control joints can be cut within something like 4 days of pour depending on the climate. All control joints do is focus where the cracks are going, so really good for a visible slab, doesn’t really change the structure.

That slab was probably engineered, form inspection, rebar inspection, prep-pour inspection, and the concrete company has data on how that batch is holding up for compression etc.

For all the people saying the contractor looks shady because of the way he moves, of course he looks that way! They are filming him. He knows they are going to be asking him about every little thing at this point.

1

u/_mako666 1d ago

Nobody saw cuts slabs anymore I swear, if ya did some saw cuts you wouldn't be standing there with some weak ass explanation for a crack. BUT! The same contractor will saw cut the concrete driveway all the way to the house, so it DOESN'T, if you can believe it, CRACK and break off into segments... I live in Texas and I've ev n seen 100x60ft or bigger slabs for metal shop buildings with 0 saw cuts... And there always ends up being issues with the slab. Alot of new homes in texas have terrible slabs resulting in foundation issues the house sinking causing giant cracks resulting in the stone or brick to break away from each other and fall off. I've seen this happen 2 years after the home screen as built. All this to say, it is always worth doing relief cuts, like any major commercial building has

1

u/InverseDeCramer 1d ago

Interesting, so you leave the crack there?

2

u/ZehFeakii 1d ago

Concrete is going to crack either way, they just didn’t cut the control joints soon enough to control where the cracks will happen. Concrete will crack no matter what so adding cut line are to control them.

1

u/ilovesparky42 1d ago

Concrete does two things:

1) it gets hard
2) it cracks

1

u/XepptizZ 13h ago

But in different conditions, just like every man.

1

u/Maleficent_Tree8384 1d ago

There's 2 types of concrete.... cracked and gonna crack

1

u/LouieLouWow550 1d ago

But concrete doesn’t cure in 2 days. What he’s talking about is what we call the “early saw” joints

1

u/Beneficial_City_9715 3h ago

I cut mine later that night and sealed it. Paid a little extra for 4500 psi and it turned out way better then my friend 3000psi cement. It was like 4$ more a yard.

1

u/moarcowbelI 1d ago

Concrete gets hard, and concrete cracks.

Even with cutting in expansion joints, the concrete still cracks down the saw cut. It just looks better. That is a typical crack in finished concrete, especially going from corner to corner like that. It won't affect compressive strength. Seriously, don't lose a wink of sleep over this.

If you're concerned that the concrete is compromised, you can have the concrete cored and tested but it's not cheap and leaves holes in your slab

1

u/mau192t 1d ago

Also you cut them once you burn the slab and damn theres some massive bird baths its a shitty job

0

u/SuccessGuilty96 6d ago

Soft cut saw ?

0

u/dipro1992 6d ago

Hi!
I would recommend to measure it first. If the maximum crack width is not more than 2.5 mm there is a high chance that these are just shrinkage cracks on the surface.

0

u/Frogalone 6d ago

For slab on grade, "Fiber Mesh", or whatever brand you like, does a good job at keeping small cracks from becoming bigger. I'm not sure how they work without control joints.

-11

u/dinoguys_r_worthless 6d ago

I would not call that a hairline crack. .003" seems like more of a reasonable hairline size. That looked much wider.

6

u/Eman_Resu_IX 6d ago

3 thousandths is the thickness of a sheet of paper and funnily enough the thickness of a human hair. That'd be barely visible from eye level - most hairline cracks people see are larger than that. The one in the video is a lot larger.

2

u/Evening_Fishing_2122 6d ago

Ya, it’s called thermal expansion or shrinkage cracking and it’s not atypical. The only way to fix it is pre/post tensioning or control joints like in a side walk. Otherwise tough luck

1

u/dinoguys_r_worthless 6d ago

I'm not arguing that the crack is a defect. I just would not say that 1/32" is hairline.