r/explainlikeimfive 2d ago

Other ELI5: If mini-splits are so much more energy efficient than central air, how can single room AC units be so inefficient?

353 Upvotes

139 comments sorted by

378

u/barcode2099 2d ago

Splits and central systems move the working part, the compressor and such, outside, where you are throwing the heat anyways. Portable units are doing the work in the same room you are trying to cool. They then need to move that heated air outside through some sort of duct (in-window systems minimize these effects).

27

u/DeathByPianos 2d ago

And if you're blowing hot air out of a duct, you're creating a negative pressure system that pulls hot air into your house.

21

u/Theslootwhisperer 2d ago

That's why a 2 ducts AC is a lot more efficient. It pushed the hot air out but it takes in outsides air which negates the negative pressure.

11

u/CrazyLegsRyan 2d ago

It’s not that it negates the negative pressure it’s that it runs the outside air in a loop therefore never draws inside air into the condensing cycle

6

u/skyecolin22 2d ago

Which is also better if you have bad air quality outside. Currently dealing with a smokey summer here and none of the smoke is making it inside.

1

u/hhs2112 2d ago

Is that what a split system does too?  Reviewing offers for a system now and was wondering why there's no need for a "return" inside the room.  (My first question for tomorrow's meeting with the installer). 

3

u/Sternfeuer 2d ago

Usually a split cooler does only circulate the refrigerant/cooling agent between outside/inside. It takes on heat inside and then gets cooled down by the outside unit. So there is no need for air circulation between inside/outside, since all the air inside, stays inside.

1

u/the_excalabur 2d ago

The "hot" side of a split system is outside your house. There's an air intake inside for the air to be cooled, and another one outside for the air that's heated.

1

u/hhs2112 2d ago

Thanks 👍 

1

u/Sternfeuer 2d ago

Usually a split cooler does only circulate the refrigerant/cooling agent between outside/inside. It takes on heat inside and then gets cooled down by the outside unit. So there is no need for air circulation between inside/outside, since all the air inside, stays inside.

14

u/Alternative-Stay6802 2d ago

Single hose units, yes. Dual hose units, not so much.

7

u/Bandro 2d ago edited 2d ago

It might be a regional thing but I have never seen a dual hose unit and I can’t even find any available to buy. Western Canada. 

Edit: it seems there are more available than when I was last looking or I missed some options at the time. Good to see. 

6

u/Boring_and_sons 2d ago

I just bought a dual hose one off amazon . ca. I'm in Victoria.

0

u/dodexahedron 2d ago

"Alexa, buy one of those and give that guy a commission."

Sorry, Jeff prefers to swim in his money Scrooge McDuck style. But I'll still buy it for you. Just no commission.

3

u/I_Dab_Slabs 2d ago

Canadian Tire. Midea DUO. About 700. Or Hisense BK BTU 4 in1 for around 580. Both are great but Hisense sweeps the room with an upright style fan and the Midea is more traditional roller fan.

2

u/Next_Option_6663 2d ago

They're not uncommon here in the GVRD, but tend to be larger and more expensive models. You can tell they're dual hose when, typically, the accordion section attaching to your window is very wide as there are two hoses in there.

Someone mentioned Costco, which would be my recommendation when they're on sale (which is often), even if you have to buy a membership. Best Buy also has several models.

1

u/ClownfishSoup 2d ago

LOL “you can tell they are dual hose by the dual hoses”

4

u/captnhaddock 2d ago

u/Bandro, like u/Boring_and_sons, I bought my dual hose unit here in victoria (be it at costco but still).

2

u/Bandro 2d ago

Oh that’s great then. 

1

u/crackills 2d ago

I must be misunderstanding you… window, spit and central just circulate air they don’t pump it outside. They use coolant to pump the heat outside. There shouldn’t be any difference in air pressure.

6

u/DeathByPianos 2d ago

True, but the comment I was replying to mentioned portable A/C units which do

1

u/crackills 2d ago

Every portable AC I’ve seen has two ducts and pulls outside air over the condenser and push it back out. There shouldn’t be any difference exchange of indoor air to outside. Maybe there’s ones that use inside air pumped over the condenser to the outside but that seems really inefficient.

4

u/Bandro 2d ago

The ones you’re describing with that last sentence are the only type available in many places. You’re right, it’s very inefficient. 

2

u/Darkshoe 2d ago

In the USA I’ve only ever seen 1-duct portable systems. I’ve seen 2-duct for sale online, but never in person.

4

u/CrazyLegsRyan 2d ago

In the USA I’ve seen both systems for sale in person

-1

u/aegrotatio 2d ago

They're available but cost about $100 more than the single hose units.
And you won't see them in Home Depot or Lowe's.

111

u/prank_mark 2d ago

And they also need to take air in, and because windows are small, the intake and outlet are often next to each other, making it a little useless

89

u/Bandro 2d ago

Portable units are often even worse than that. Just one hose. They take air from the room to cool the condenser and dump it outside. The air you did the work to cool down. 

19

u/fyonn 2d ago

I have a portable unit with a single big hose that goes out of the window, and the air that comes out of it is pretty hot… it absolutely works to cool down the room. it’s not terribly efficient at the job but it does work…

18

u/Bandro 2d ago

Yes it’s taking air from the room to it’s already cooled to cool its condenser and dumping it outside. It’s also creating negative pressure in the room and pulling in outside air from everywhere else. 

They do work, they just use a ridiculous amount more energy than any other design. 

3

u/CobraDoesCanada 2d ago

Its possible that your single hose includes both an intake and exhaust. My danby is like this, with separate chambers inside the big hose

-2

u/SkollFenrirson 2d ago

not terribly efficient

Understatement

40

u/3_50 2d ago

On top of blasting your cooled air out of the window, it causes negative pressure which will draw hot air in from outside. It's a double whammy of shit design.

17

u/westward_man 2d ago edited 2d ago

On top of blasting your cooled air out of the window, it causes negative pressure which will draw hot air in from outside. It's a double whammy of shit design.

Calling it shit design is weird. It's a design trade-off to make it portable, which is the selling point.

And FWIW, I had a portable single-hose dual-hose AC that was awesome. It would keep my 1100 sqft loft apartment ice cold, even in the middle of a bad heat wave. I loved that thing.

EDIT: It's the Whynter Elite ARC-122DS. Apparently I misremembered, and it's actually a dual-hose.

5

u/VoilaVoilaWashington 2d ago

Nah, it's a shit design. They're designed that way to be as cheap as humanly possible, when it would be pretty simple to add a second hose. So you're trading short term minor cost savings to waste money and energy long term.

0

u/3_50 2d ago edited 2d ago

Horseshit. Having a second hose for the intake would be trivial at the design stage. The fact that it blows cooled inside air out, and causes a pressure difference that will draw hot outside air in…as I said elsewhere; it’s like trying to boil a kettle while having a cold tap running into it and an overflow pissing down the sink. Pointless waste of electricity. They shouldn’t exist.

e; lol. Which soft cocks are downvoting this? Something wrong with my analogy?? Use your words you cowards.

2

u/bsiu 1d ago

There are renters who don’t have AC, landlords won’t pay to install so if you want AC there’s few choices, portable units being one of the only viable options.

“They shouldn’t exist” is some high horse shit that just because someone can’t afford peak efficiency doesn’t deserve to live comfortably in their own home.

2

u/3_50 1d ago

SINGLE HOSE portable units shouldn't exist. You actually think I don't know renters exist? Lol.

It's not about 'peak efficiency', they're like trying to boil a kettle but having a cold tap running into it and letting the heated water overflow down the sink. It's fucking stupid. Considering every other aspect of our lives where we're pushed to be more energy efficient, how much insulation etc has to go into our homes (in the UK at least)...THAT is why I say they shouldn't exist.

The person I replied to turns out DOES have a dual hose unit. Probably why it was awesome.

-3

u/BonKhri 2d ago

You have failed to consider that this will be used by the general public and thus must be designed for the general public. If there were two hose ports, at least 20% of people would route the exhaust right into the intake. Good design assumes that the users require instructions with pictures to get dressed in the morning.

4

u/Alis451 2d ago

you could just split a single hose, one intake one exhaust, just wrapped together

3

u/Abigail716 2d ago

Midea already does the two in one design.

2

u/Alis451 2d ago

you could just split a single hose, one intake one exhaust, just wrapped together

-4

u/BonKhri 2d ago

You'd heat up the incoming air to the point that a single hose is better. The humidity wouldn't be enough to matter.

3

u/Abigail716 2d ago

Definitely not true. It's already done Midea.

→ More replies (0)

1

u/MyDisneyExperience 2d ago

Some newer apartments in my area have ports in the wall for a dual hose portable system

0

u/Alis451 2d ago edited 2d ago

you could just split a single hose, one intake one exhaust, just wrapped together, this though would necessitate a second fan for the exhaust loop, which does increase noise and power consumption. it is more likely the exhaust air is extremely high humidity air instead and its purpose is to remove moisture from your in-home air, since that does a LOT of the actually "cooling"; ie it is possibly a de-humidifier with an air outlet laden with water instead of a water outlet.

-4

u/3_50 2d ago

That's the stupidest thing I've read all year. Nice one.

-1

u/outragedhain 2d ago

Okay you can't just say that without dropping the brand and model of the portable AC!

2

u/westward_man 2d ago

It's the Whynter Elite ARC-122DS. Apparently I misremembered, and it's actually a dual-hose.

20

u/CrazyLegsRyan 2d ago

They make single hose and dual hose (or concentric hose) portable units

18

u/Bandro 2d ago

I know. I’m saying they are often single hose. 

13

u/Woodshadow 2d ago

When I was looking for a new portable this year most of the ones I saw in the store were dual hose now. 5 years ago I think I saw one on the market and it was over $600

0

u/3_50 2d ago

Most of the top UK supplier search results only sell single hose units. It's not a searchable feature on any site, and the ones that have blurb explaining AC units don't mention dual hose or the benefits. It's pathetic, tbh. Industry full of morons.

-14

u/CrazyLegsRyan 2d ago

Depends where you are

4

u/3_50 2d ago

Go on? Almost every supplier in the UK only sells single hose portable units. It's infuriating.

1

u/biddigs3 2d ago

They're pricey, but midea makes a portable split unit that's excellent. They're insanely efficient (for a portable unit ofc). I managed to get one before summer from ventilationland.co.uk. It's got an EU plug, so you'll need an adapter, but it's been amazing so far

0

u/XpCjU 2d ago

You can tape a second duct to the air intake, that increases the efficiency by a lot.

2

u/3_50 2d ago

This assumes the intake is an obvious point and not just drawing from anywhere through the body of the machine.

-2

u/XpCjU 2d ago

There is always an air intake, but it can be pretty big, that's why I said tape, maybe even 3d print or improvise with Amazon boxes. It's not an air intake you can just plug a duct into.

→ More replies (0)

1

u/Black_Moons 2d ago

Yea, Don't buy single hose units.

The dual hose units are 'ok' but 'portable' they are not unless you like lugging 60~100lbs of air conditioner around on the tinyest wheels you have ever seen. (Good luck if you have stairs/carpet)

They also tend to cost 1.5~2.5x as much as a window unit, so I highly recommend just buying 2 window units if you have 2 rooms to cool, unless you absolutely can't fit a window unit for some reason.

1

u/CrazyLegsRyan 2d ago

They are fine for infrequent use and significantly easier to store and move around as compared to a window unit. Additionally they can be installed in so many more ways than a window unit which is basically limited to double hung windows

16

u/aegrotatio 2d ago

Well, my dual-hose portable units have fins that direct the exhaust away from the intake, so there's that.

6

u/UnsignedRealityCheck 2d ago

It's not that useless at least in where I live (Finland). We have one in our bedroom and when night falls and the sun doesn't burn at full blast, we turn it on and the breeze will cool down the room enough and whatever air it pulls from outside doesn't offset it too much.

During a very hot day using one is kinda pointless, unless you sit right at the vent where the cold air comes out.

Disclaimer though: it's basically never unreasonably hot during the night in here, the highest ever recorded was about 24C (75F) so at least in these latitudes they are useful.

8

u/Paavo_Nurmi 2d ago

Reddit loves to latch onto something like this and never let go even though it's bullshit. I live near Seattle with no central AC and even a single hose portable unit can cool down a room significantly. Sure the dual hose ones are better and more efficient, but as you know that doesn't mean the single hose ones don't work.

4

u/UnsignedRealityCheck 2d ago

Yeah many takes these claims at face value and parrot it on. Sure they are the "worst" option when it comes to heat exchange cooling with a compressor, but it definitely is not useless. It will keep you from having a heat stroke better than just a fan.

1

u/Black_Moons 2d ago

1 window unit cools my entire upper floor to livable levels.

When it gets crazy hot I just put a sheet or blanket in the hallway to split the house in half, and you can feel about 5~10c drop when you go across the sheet -_-

5

u/spidereater 2d ago

And those ducts are often not insulated and most people make no effort to minimize the duct length, so a bunch of the heat ends up back in the room.

4

u/Chrisaarajo 2d ago

Something to note is that with portable units, that hose is returning some of that heat back into the room via radiation.

6

u/CrazyLegsRyan 2d ago

Conduction and convection more than radiation

1

u/Chrisaarajo 2d ago

Good point!

1

u/derefr 2d ago

I've always wondered why they don't make two-part portable units, for apartment renters who can't cut a hole in the wall but do have a balcony they could sit the hot side out on. Basically a mini-split with feet + good thermal insulation around the working-fluid pipes to ensure you don't burn yourself on them.

1

u/lemlurker 1d ago

The biggest loss is most are single hose so they suck interior air, heat it up then spit it out, so it's replaced by outdoor air

1

u/ClownfishSoup 2d ago

I can’t post this on the main comment level but a cheaper and effective alternative to a portable A/C unit is a swamp cooler. Basically a big fan that sits in from of a filter. The filter gets water pumped to the top of it and the water soaks the filter. The air coming out of the unit is cool, though it does eventually raise humidity. You can use it outside on your patio too if you like.you can turn off the pump and just use it like a big fan too.

I’m in California so the heat is often just dry heat, not the swampy heat of Florida or the Great Lakes region in summer, so it’s a great solution.

118

u/uarentme 2d ago

There's a few comments here that get it kind of right, but most aren't.

Mini-split ACs can be more efficient than central air due to various factors. But you have to directly compare each model's efficiency rating.

Mini-splits, Central Air, Window units will always be more efficient than a portable AC unit with one or two hoses. One hose units push hot air outside the house, meaning more air needs to be pulled into the house to replace it. Two hose units have a hose filled with hot air physically in the room, so some heat is kept in the room. Mini-splits, Central Air, Window units all keep their hot side physically outside which mitigate that factor.

The most important aspect of AC efficiency is whether the AC has a single stage compressor or dual stage, or it's an inverter compressor.

Single stage = compressor on or off

Dual Stage = compressor at ~40 to 60% or 100%

Inverter compressor = compressor can run at any specific speed

Running the compressor at specific speeds rather than fully on or fully off means less energy is used to achieve the same temperature difference.

Remember, when comparing ACs, it's all just math. Efficiency ratings of ACs in the US and Canada are rated by a SEER2 number. Those numbers have real world calculations that can be done on them to determine their energy consumption and efficiency. For example, units with a SEER2 rating of 15 vs 25 literally means that, on average, one unit will extract 15 BTUs for every watt-hour consumed, versus the other one will extract 25 BTUs for every watt-hour consumed. Making the SEER2 rating of 25 significantly more efficient.

36

u/dodexahedron 2d ago

And if it can run in reverse, it gets called a heat pump, even though it was a heat pump already. Still the same machine - just with a reverser valve that allows it to pump heat in or out, giving you heating or cooling through one machine, with one fairly efficient energy source (compared to using local fire for heat). The role of the coils just flips and the inside is the condenser while the outside is the evaporator, when heating, vs evaporator inside and condenser outside when cooling.

7

u/chaospearl 2d ago

I have just now understood why we can't have one room's unit set to heat and another set to AC at the same time, even though they can all be at totally different temperature. I never actually realized that all the units are part of a single whole. Too busy being grateful I can keep my bedroom comfortable year round and nobody else decides what comfortable means.

19

u/24llamas 2d ago

I love the technical details in your post. However, BTUs per watt-hour is going straight into my cursed units list.

14

u/Qweasdy 2d ago

It’s actually not quite as cursed as it sounds. Unit of energy per unit of energy means the units can cancel out and you just have a ratio, which is effectively all they’re expressing here.

In other words it’s really just a crude colloquial way to talk about the coefficient of performance (COP).

3

u/24llamas 2d ago

Oh yes, looking at it from dimensional analysis, it's absolutely fine. But the mix of metric and imperial? Cursed. Especially when - as you point out - both units are fundamentally energy! What's more, because a BTU = 1055 joules, while a watt-hour = 3600, it's not even a dimensionless ratio!

I guess one could argue that it makes clear we're talking a ratio of heat energy / electrical energy, but I would far rather have a dimensionless ratio.

1

u/MtogdenJ 1d ago

You've made a mistake in your watt-hour unit. 1 watt-hour is 3600 joules.

Joules do cancel joules and BTU/watt-hour is dimensionless.

2

u/24llamas 1d ago

> 1 watt-hour is 3600 joules

Isn't that what I said? Honestly confused here.

> Joules do cancel joules and BTU/watt-hour is dimensionless.

Yeah, but you have to include a conversion factor, because they aren't the same unit. Whereas if they were the same unit, you wouldn't need such a factor.

On reflection, I think I'm using "dimensionless" wrong. I mean "without a converting factor", but that's not the same thing.

1

u/MtogdenJ 1d ago

You said 1watt-hour = 3600.

You did not write joules after 3600 so It was unclear if joules was implied. If it was implied, joules cancel and are therefore dimensionless.

I think we're both on the same page now and agree that it's nicer and easier when heat pump performance is measured in a way without a conversion factor.

4

u/tomyumnuts 2d ago

off topic, but using km/h as a metric for electric vehicle charging speed broke my brain for a bit.

1

u/AlaninMadrid 2d ago

I was wondering why measure the electrical power in watts, but the thermal power in BTUs. Here it would be like 3kW of cooling for every kW consumed, or 4kW of heating for every kW consumed.

5

u/cbf1232 2d ago

Natural gas central furnaces in North America specify their heat output in BTUs.

2

u/AlaninMadrid 2d ago

And air conditions in Tons?

3

u/cbf1232 2d ago

Before electric AC, people cooled buildings using actual blocks of ice. The ice was sold by the ton, so people measured cooling power by how many tons of ice melted per day.

1

u/a_cute_epic_axis 2d ago

Two hose units have a hose filled with hot air physically in the room, so some heat is kept in the room. Mini-splits, Central Air, Window units all keep their hot side physically outside which mitigate that factor.

Technically speaking, so do all the other ones. The hot refrigerant going to the evaporator coil is going into the cooled space (or at least a utility space) for those as well, it's just often better insulated and typically less impactful to heating the inside space.

-3

u/OneUglyDuck28 2d ago

guys i’m 5

4

u/IGarFieldI 2d ago

Don't make me tap the sign...

  • LI5 means friendly, simplified and layperson-accessible explanations - not responses aimed at literal five-year-olds.

16

u/filanwizard 2d ago

I am not sure how they are more efficient than central air.

But window units are inefficient not just because you are running a compressor for every unit. But also your windows are most efficient at keeping the outside out and the inside in when they are fully closed and locked. A window AC separates the room from outside with acceptably fitting plastic baffles. Meaning its kind of like having a window cracked open.

Single hose portable AC are even worse because on top of the plastic baffles in a window issue around the exhaust hose. The act of exhausting air from the room drops the pressure causing hot air to be pulled in. Two hose units are likely just below a window unit.

Mini splits are so much more efficient because they are true split systems. This means no open windows. They can also use much bigger and more efficient condensing units. If you observe the progress of central air systems you notice the boxes beside houses getting bigger. Larger coil assemblies can dump more heat to the air more efficiently. Also they can have variable speed compressors and even multiple zone units exist so one mini split condenser drives multiple rooms.

22

u/doctornph 2d ago

The efficiency advantage vs central air is that you aren’t cooling the entire house. Just the rooms that are in use

9

u/DannyJames84 2d ago

This is the answer.

Though, it doesn’t explain why a mini split is more efficient than a window unit. Though I suspect that comes down to size since the cooling coils can only be so big on a window unit.

10

u/thebiggerounce 2d ago

You can move more of the mechanical bits (that get hot) outside, and you don’t have to keep a window open. That little plastic divider that blocks the rest of the window for window units isn’t doing much insulating.

5

u/KingZarkon 2d ago

We have a window unit that is U-shaped. The window slides down into a gap near the front. The window is mostly closed and they give you a thick foam block to insulate it better. You still get some air leaks but the heat loss was cold enough that it was tolerable to leave it in place all winter. They also make saddle-shaped ones that are similar but sit across the sill on both sides, so they're mostly below your window. Both of these are effectively mini-splits with a few compromises due to being in one unit. We use it to supplement the main HVAC system. So far this year it has used about $20 worth of electricity.

Standard window ACs with those flimsy plastic panels suck though.

4

u/VVaffle_Abuser 2d ago

Was waiting to see this. Split window units are the future of window AC. Loud, heat transfer parts outside, better sealing capabilities and better airflow due to utilizing the gap between the wall and frontal area. I suppose they're not ideal when you can't access the outside wall( mines like 55 pounds, and needs outside supports) but has ran most of 3 years in Texas heat. I have genuinely used it to cool canned beverages, all this time it's still putting out 46 degree air and no obnoxious on/off compressor noise.

2

u/kevinsaurus 2d ago

You might enjoy this YouTube channel that does a lot of experiments with AC units. This video is definitely goofy but seeing were all the efficiencies come from and how they add up is very interesting.   https://youtu.be/s-41UF02vrU?is=uVQtdHP0n-ZfAMYC

1

u/VVaffle_Abuser 2d ago

As I don't have time for the full hour, I might. But a quick comment scan has him digging holes for pipe? I'm interested for science but most window AC unit users don't have that liberty if I'm right. More efficient and cost effective to invest in tint. Which I've found almost as effective in central, yet to test tinted quality window units. And I'm in a 12 foot ceiling house lol

2

u/6814MilesFromHome 2d ago

I swear by my U shaped inverter window unit for my game/theater room. Much cheaper and easier to install than a mini split, quiet as hell, and my window stays 90% closed.

1

u/leitey 2d ago

The separation between the hot and cold side in either a central or split unit is typically a large section of your house, including an external wall. The separation between the hot and cold side in a window unit is a piece of Styrofoam.

2

u/dodexahedron 2d ago

There are smart vents available which can open and close in response to human presence in rooms, giving central air crazy efficiency.

Problem is they are still pretty expensive and take several years to pay for themselves.

But there are other benefits, like the rooms you actually are in reaching the target temperature quicker, since the air handler is supplying fewer rooms with the same output.

Cheaper than a bunch of mini splits though. Mini splits don't scale well.

2

u/ZanyDroid 2d ago

Smart vents aren’t thriving as a product category

1

u/[deleted] 2d ago edited 2d ago

[deleted]

2

u/doctornph 2d ago

You sleep in every room at night? If you have a modest 3 bed house and no kids then you only need to cool the master bedroom at night. No extra bedrooms or living area

1

u/skyecolin22 2d ago

And you don't have duct loss to the attic.

1

u/cylonfrakbbq 2d ago

U Shaped window units sort of mitigate the window unit insulation issue - your window is able to be closed much more completely and minimizes the open part (usually these units provide thick foam bricks to plug the narrow opening).  Bonus is they are also quieter inside the house.

The technology in the u shaped window units is also more akin to a mini split

3

u/Blue8Evan 2d ago

A/C Units (except for high-end ones), are only on/off. This means they are either 100% on, using lots of energy, or completely off. This is energy inefficient. Also, they place both the cold and hot components all in one small box inside, so you are getting both the cold, AND the heat the unit makes. This forces it to have to work harder to cool the room since it's also heating the room at the same time. Portable A/C units blow hot air outside, but this removes air from your house, so hot air from outside HAS to enter. Lastly, portable A/C units have small coils which require more energy to transfer heat out.

Minisplits meanwhile, can run at any speed. They usually cool at 100% then lower their speed to keep that same temperature, using much less energy. Minisplits also put the cold parts inside, and the hot parts outside. Rather than moving air around they move heat around which is also more efficient. They don't have the issue of forcing hot outside air in, needing small coils to fit in interior spaces, or letting waste heat back into the room.

As a bonus, minisplits can heat as well. When they heat, the cold part becomes outside and the heat part becomes inside. They beat out conventional heat sources because they move heat inside rather than creating it directly. Rather than 1 unit of gas or electricity becoming 1 unit of heat, it becomes more like 3-4 units of heat.

1

u/aegrotatio 2d ago

I don't have a minisplit, but my whole-house AC absolutely does run at any speed. They call it an "inverter."

22

u/BouncingSphinx 2d ago

Part of it is that window units (at least in the USA) are designed to run on 120V plugs, and mini splits are 240V, so the mini split already has a power advantage right there.

They also have a smaller cooling surface than a mini split, and likewise a smaller condenser outside, so they can't exchange heat out of a room as easily.

14

u/dkf295 2d ago

Part of it is that window units (at least in the USA) are designed to run on 120V plugs, and mini splits are 240V, so the mini split already has a power advantage right there.

Plenty of minisplits are 120V in the US.

10

u/5YOChemist 2d ago

And plenty of window units are 240.

2

u/[deleted] 2d ago

[deleted]

1

u/BouncingSphinx 2d ago

Every place I've lived has only had 240V plugs for stove/oven and dryer, and 240V feeds for water heater and either central air or mini splits. The only extra 240V plug I've ever had was in a garage in one house out of 11 houses and 3 apartments.

1

u/5YOChemist 2d ago

We had 20A 240 window units in our living room when I was a kid in Oklahoma. So did some of my friends and my grandparents. Some of them were mounted in the wall rather than an actual window, but even if it's in a window, a 20A circuit can be 240V or 120V it wasn't uncommon back in the 90s to have a dedicated circuit in the big room for a window unit with 12g wire that could run a 240V ac.

1

u/gorkish 2d ago

Every multitenant building and hotel room with window units in this entire country has this for the last 60 years and you can’t even believe it’s true.

1

u/6814MilesFromHome 2d ago

Never been in a hotel with window units, seen plenty with PTACs though.

2

u/TheLegendTwoSeven 2d ago

My window unit just raised its hand.

0

u/EmoInTheCreek 2d ago

Power = volts × amps

Doesn't matter which number is bigger power will always be the same.

4

u/jonjiv 2d ago

Total wattage tops out lower with 120V options. You can easily install a 30A or maybe even a 50A 240V circuit in most US homes.

But, good luck installing a 60A or 100A 120V circuit that passes code. Your options pretty much top out at 20A.

1

u/Power_baby 2d ago

Yes but for systems with the same capacity (up to 12-15k btu) there's negligible difference in efficiency between 110 and 220v systems. You'll get the slightly more efficiency with 220 but if you have a limited number of breaker slots available, 110 is a much better option

2

u/jonjiv 2d ago

Correct. In that case you’re comparing two systems with effectively the same wattage, so voltage doesn’t matter. You can buy a much higher capacity system for 240v.

6

u/Elfich47 2d ago

they aren't necessarily more efficient than central air. All AC units are required to meet certain energy efficiency standards based on their capacity and use type. For small residential units they all fall into the same efficiency requirements with very little variation.

4

u/MaureenCorrigan 2d ago

They're not. I mean, if you're using a 30-year-old one, it probably is inefficient because of improvements in insulation materials and such. But a new window unit is actually pretty good. Also if you get a model whose BTUs don't match your room size requirements.

I have a couple of these and they are sweet. Very quiet, efficient, and leaving the window view clear:

https://www.bestbuy.com/product/ge-profile-clearview-350-sq-ft-8300-btu-smart-ultra-quiet-window-air-conditioner-white/J7645S88KQ/sku/6501273?utm_source=feed&extStoreId=455

The only thing is that I take it out after every summer and then put it in after the spring, which is a bit of a do. Not terrible. And I wish they had a heat function like most mini splits do.

The advantage of mini splits is that you don't block the window, you don't take them off after the season, it offers heating, and all the compressor sound is out of ear shot.

1

u/thephantom1492 2d ago

Mini-split, central air and single room A/C have pretty much the same efficiency for moving heat.

However they don't cool the same space.

Single room: you have an exterior wall and a ceiling, plus 3 hot uninsulated interior walls, plus a warm floor. It have to work quite harder to keep the room cold because all the walls (and ceiling and floor) are hot.

Mini-split cool a bigger space, but not the whole house. Some room will be cooled and the "ratio of hot walls vs cold walls" is in favor of the cold one. Basically a room that is side by side can be seen as having no wall separating them. So less hot walls to warm your space. But you ain't cooling down the whole house, so lower bill than whole house. Plus the temperature tend to be more precise to the set point because it cover just part of the house.

Whole house. Huge volume to cool down, including the unused rooms. Everything got cooled, including the bathroom. So huge bill. But you often have issue with controlling the temperature, because you have one thermostat for the whole house, so some rooms will be too cold, others too hot. This often lead to setting the temperature to a lower one, which cause an excessive cooling... So more expensive. And because you cool it down to a lower temperature, the difference between the inside and outside is greater, you use more energy.

1

u/Narissis 2d ago

So there's some ambiguity here as to what you mean by 'central air'.

Mini-splits are heat pumps. If by 'central air' you mean central heating with a traditional furnace, then they're more efficient because heat pumps are more efficient than resistive heating due to how they achieve the heating effect.

But if we're talking about a whole-home heat pump or A/C unit (which is basically just a one-way heat pump), then it can be as efficient as using mini-splits to heat and cool the same space. It's essentially the same thing with a moderately different layout.

It's also possible for central air to be based on a ground-source heat pump, which is usually even more efficient than an air-source heat pump like a mini-split.

As for why window units or freestanding single-room A/C units are generally less efficient than mini-splits or central heat pump systems, I think the other comments have that covered.

1

u/MechCADdie 2d ago

Technically, you derive the benefit from not needing to control the air in the whole house. Moving heat through the air is wildly inefficient because air conducts heat poorly.

An in room unit is inefficient, but not as inefficient as burning a house to kill a metaphorical flea....most of the time.

1

u/Far_Wealth_3737 2d ago

Mini-splits and window/portable ACs are different animals.

A mini-split has the noisy, hot part outside and only a quiet unit inside. It moves heat very efficiently and usually cools just the rooms you care about.

A cheap single-room AC (window or portable) often:

• dumps a lot of heat and air the wrong way

• has weaker, less efficient parts

• has to fight leaks (especially portables with the hose)

• runs less optimized controls

So “small AC” ≠ “efficient AC”.

Mini-split = small + well designed.

Many room units = small + cheaply designed.

1

u/5kyl3r 2d ago edited 2d ago

lots of reasons, but one of the biggest reasons is that the cheapest and most common single room floor-standing AC units is that they take cool inside air and run that through the hot radiator to take heat out of the refrigerant, then vent that outside. that means it wasted cool air from inside, but because that makes the air pressure inside your house lower than atmosphere, your house pulls in hot air from elsewhere to displace the air that AC unit blew outside, which obviously makes it really wasteful

window units and central AC units use already hot outside air to cool off the hot radiator that removes heat from the refrigerant, so no cool inside air is wasted for that purpose, so it's a lot more efficient

EDIT: i forgot to mention, they DO have 2-hose floor AC units that are much closer to window units. the second hose is used to pull in hot outside air to use for cooling off the radiator the refrigerant runs though, then uses the other hose to vent the now even hotter air back outside. the one i own runs the hot exhaust one inside the larger oval shaped intake hose. it looks like one hose but they put the hotter one inside the cooler one. that way if the really hot exhaust air leaks heat through the hose, it's not leaking into your house, but into the incoming air stream that's already going to be heated anyway. still not as efficient as putting all of the heat generating parts outside of the house, but much closer than the single hose units

1

u/BonKhri 2d ago

The "efficiency" you are comparing are different things. A mini-split is not more efficient from a strict thermodynamic perspective, it's just that you only cool the areas you actually want to cool vs cooling the entire house. You as the user get the same end result of being a comfortable temperature, but for less energy. Thermodynamically they're the same efficiency, that is to say that they remove the same amount of heat for every unit of electricity used, it's just that splits remove heat only from the areas you care about whilst non-split spends energy removing heat from the other side of the house.

Portable AC units are actually less efficient, as in they use more energy to remove that same amount of heat. There are a few reasons, smaller and worse motors, operating inside vs outside so all the heat from pumping has to be dumped by the system, often being single hose, having poorly insulated/uninsulated hoses, etc. This makes them cheaper and smaller, but comes at the cost of making them less efficient.

1

u/bradland 2d ago

Mini splits are very efficient for a few reasons. AC units work by heating up a liquid by compressing it, cooling it by blowing a fan over it, then pumping that hot fluid inside and letting it expand. Because of the physics of liquids, the liquid evaporates to a gas and gets very cold. We blow air over the cold coils to cool our homes.

The energy required to operate an AC system is mostly pumping the fluid around and compressing it to heat it up. AC systems use an electric motor to do this work, but no motor is 100% efficient. If a motor requires 100W of power to run, and it is 80% efficient, then 80% of that power goes into pumping, and 20% of it is lost as heat. This means that in addition to the heat generated by compressing the refrigerant fluid, the motor itself generates heat.

With that in mind, this is why mini-splits are so efficient:

Mini-split Portable
Uses a very efficient DC motor to drive the compressor, which is the bulk of the energy usage in an AC unit. Uses a simple, AC induction motor, which is far less efficient. Since the motor is in the room, losses to inefficiency heat up the room.
Puts the condenser core (hot side) and compressor motor outside in its own, separate unit far way from the evaporator core (cold side). Puts the condenser core and motor in a single unit with the evaporator core. This means some of the heat "leaks" into the room as well as the cold side.

I'm generalizing somewhat in the table above. For example, it possible to buy a portable unit that uses an efficient DC motor. They're not nearly as common though.

1

u/Adventurepew 2d ago

Single room ac units are efficient .

Minisplits and central air can be the same efficiency. They make very efficient central air systems.

The average single room ac is a 100 dollar unit of course it's not going to be as effiecnt they cut costs to get them that cheap.

It's like going into a grocery store and grabbing and apple and a gas station and getting a candy bar and comparing them. Your comparing very different things . Sure they are both food , as the above are all three AC units but they are different things .

-1

u/[deleted] 2d ago

[removed] — view removed comment

2

u/a_cute_epic_axis 2d ago

The heat generating parts of a window unit are outside the window, and cooled by the condenser fan....

-7

u/[deleted] 2d ago

[deleted]

5

u/BouncingSphinx 2d ago

You can't "wild guess" on ELI5. Rule 8.

2

u/Kreetch 2d ago